Instrumentation Specialist Question:

Do you know how can a D.P. transmitter be calibrated?

Tweet Share WhatsApp

Answer:

D.P. transmitter can be calibrated using following steps:
1. Adjust zero of Xmtrs.
2. Perform static pressure test: Give equal pressure on both sides of transmitter. Zero should not shift either side. If the zero shifts then carry out static alignment.
3. Perform vacuum test: Apply equal vacuum to both the sides. Zero should not shift.
4. Calibration procedure: Give 20 psi air supply to the transmitter and vent L.P. side to atmosphere. Connect output of the instrument to the standard test gauge. Adjust zero. Apply required pressure to the high pressure side and adjust the span. Adjust zero gain if necessary.

Download Instrumentation Specialist PDF Read All 109 Instrumentation Specialist Questions
Previous QuestionNext Question
Do you know what is the working of Rota meter?Explain difference between transducer and converter in instrumentation